Many thanks to Toby Grotz for sharing these two files on the critical subject of grounding and bonding of electrical circuitry. My main interest in this stems from personally witnessing a very large transformer explode from the ferroresonance phenomenon. The faulty grounding of power distribution systems up in dairy farming area of the mid West where cattle were electrocuted added to my interest. When the huge HVDC transmission distribution systems came on line, there seamed to be a complex set of problems introduced especially in the single line type of system which relies on an earth/ocean return path. I believe you can see the unique set of problems here. See Ole and Fredric Fletcher, pay attention to the polarity and methodology of transmission of the HVDC. Remember the articles regarding the earth ground return problems up in dairy country, Wisconsin where cattle were being electrocuted by poor grounding systems in rural electric grid. I can recite a real life problem with imposing a potential into the earth on the dealing with ground return. One of our Nursing facilities had three separate buildings that shared a two pipe chilled / hot water system with buried steel 4 inch lines (supply/ return). The electrical system was 480VAC backbone with delta/Wye step down transformers which gave a base 208VAC with center tap ground for 120VAC. The facility operated just fine for 50 years. Along came an Electrical Contractor that installed a new distribution transformer (100 KVA) during an upgrade to one of the out buildings. After operation for several years the buried 4 inch steel AC/heating lines developed leaks and sections of the removed lines showed electrolytic (galvanic) erosion. I discovered that the Contractor had installed a delta/delta step-down (100 KVA) transformer and grounded one (L-2) of the Secondary terminals to get a neutral buss common for 120VAC. A huge NO,NO cause you had a potential of 230V to earth ground. The difference in ground potential between buildings created the galvanic erosion because there was a ground return current back to the 480/208VAC backbone in the mains building. This was a huge lesson on the problems encountered with relying on earth ground return path. https://www.electronicshub.org/high-voltage-dc-transmission-system/ https://circuitglobe.com/different-types-hvdc-links.html See attached files.
[2/2] Re: The subject was grounding
2019-04-16T12:27:02+00:00
·
onielsen2000
<[email protected]>
Message-ID:
<[email protected]>
Hi Norman, "I discovered that the Contractor had installed a delta/delta step-down (100 KVA) transformer and grounded one (L-2) of the Secondary terminals to get a neutral buss common for 120VAC. A huge NO,NO cause you had a potential of 230V to earth ground." Was the ground wire also used as neutral for carrying current? The ground wire must be used only for safety in case of some other insulation failure putting a person between a phase and ground. The ground wire should carry no current when no fault condition exists. Connecting one of the phases to ground should give no problem if it is only used as neutral. But physical earth must exist separate from the neutral line even though they are at the same neutral ground potential. As I understand in the US there are two phases 180 degrees out of phase. This won't work with the above way of connection with two phases out of a three phased transformer. Here each phase is 120 degrees apart from each other. Thus the voltage between two phases is square root 2 times the voltage of a single phase to neutral. Neutral of course doesn't exist in the delta connection. Three similar loads connected in star connection can make a neutral reference point for measuring the phases to neutral (of the three phases). Regards Ole ---In [email protected], <nwootan@...> wrote : Many thanks to Toby Grotz for sharing these two files on the critical subject of grounding and bonding of electrical circuitry. My main interest in this stems from personally witnessing a very large transformer explode from the ferroresonance phenomenon. The faulty grounding of power distribution systems up in dairy farming area of the mid West where cattle were electrocuted added to my interest. When the huge HVDC transmission distribution systems came on line, there seamed to be a complex set of problems introduced especially in the single line type of system which relies on an earth/ocean return path. I believe you can see the unique set of problems here. See Ole and Fredric Fletcher, pay attention to the polarity and methodology of transmission of the HVDC. Remember the articles regarding the earth ground return problems up in dairy country, Wisconsin where cattle were being electrocuted by poor grounding systems in rural electric grid. I can recite a real life problem with imposing a potential into the earth on the dealing with ground return. One of our Nursing facilities had three separate buildings that shared a two pipe chilled / hot water system with buried steel 4 inch lines (supply/ return). The electrical system was 480VAC backbone with delta/Wye step down transformers which gave a base 208VAC with center tap ground for 120VAC. The facility operated just fine for 50 years. Along came an Electrical Contractor that installed a new distribution transformer (100 KVA) during an upgrade to one of the out buildings. After operation for several years the buried 4 inch steel AC/heating lines developed leaks and sections of the removed lines showed electrolytic (galvanic) erosion. I discovered that the Contractor had installed a delta/delta step-down (100 KVA) transformer and grounded one (L-2) of the Secondary terminals to get a neutral buss common for 120VAC. A huge NO,NO cause you had a potential of 230V to earth ground. The difference in ground potential between buildings created the galvanic erosion because there was a ground return current back to the 480/208VAC backbone in the mains building. This was a huge lesson on the problems encountered with relying on earth ground return path. https://www.electronicshub.org/high-voltage-dc-transmission-system/ https://www.electronicshub.org/high-voltage-dc-transmission-system/ https://circuitglobe.com/different-types-hvdc-links.html https://circuitglobe.com/different-types-hvdc-links.html See attached files.
← Previous
Page 1 of 1
Next →